Hi,
Havent had hot water or heating since sat am. Boiler keeps tripping out and after reset keeps for about 20-30 secs and goes off again (trips)
Sounds like the pump not kicking in. I have the above pump and it was set to 2. turned it to 3 and it the whole system worked straight off? Boiler started and everything seems to be okay.
What are three 3 settings (i find in web searches that it is different speeds for different systems) but if it works now, is that bad?
thanks for any advise!