And never got to the bottom of it-
This time it's an Alpha 240p.
Gas rate fine, modulates fine, new DHW sensor even though ohms ok on old one but changed it anyway, flushed out plated exchanger twice with drain cleaner, it's def clean, diverter not passing, but at 9lts a min only getting approx 44deg at the tap, it's only feet away so not losing in distance, cold coming in at approx 12deg so temp rise only approx 32deg.
Did find why rads a ******* to heat, CH filter badly blocked, I'm wondering if the main gas to water exchanger is dirty ?
This time it's an Alpha 240p.
Gas rate fine, modulates fine, new DHW sensor even though ohms ok on old one but changed it anyway, flushed out plated exchanger twice with drain cleaner, it's def clean, diverter not passing, but at 9lts a min only getting approx 44deg at the tap, it's only feet away so not losing in distance, cold coming in at approx 12deg so temp rise only approx 32deg.
Did find why rads a ******* to heat, CH filter badly blocked, I'm wondering if the main gas to water exchanger is dirty ?