Hager SPD (SBP015N) showing red

Joined
20 Jan 2016
Messages
114
Reaction score
13
Country
United Kingdom
Hi

Yesterday we had a brief power cut for a few seconds. Apart from finding I was now the lucky owner of two dead computer monitors, on inspection of everything else I see that the Hager SPD's in my CU are showing red on the indicator panels. Hager say they are "end of life" - so does that mean just ONE power surge and these things need replacing? The SPD is only about 8 months old!

There's 2 modules and I presume SPB015n refers to the replaceable module not the complete kit? Seems though that the replaceable modules are about £100 each (I have two of them) whereas the kit which includes those modules is about £35. I saw the modules on ebay for about £16 but think I'll wisely avoid that as you don't know if someone has fiddled with them.

Should these things last more than one surge or was I really unlucky to have a major surge that wiped them out? The CU lid needs removing for replacement, but can this be done with the circuits still live?

Thanks
Dave
 
Can you post a picture of the board, showing the devices in question?

I'm surprised that there would be two SPDs in the one consumer unit, that seems odd.

To answer your other question, yes, definitely avoid the cheap Ebay fakes, but you would need to switch the main switch off before fitting the new ones (or the individual MCB, if it has one)
 
Last edited:
Should these things last more than one surge
Yes, and they do.

was I really unlucky to have a major surge that wiped them out?
Exactly.

but can this be done with the circuits still live?
NO - the whole lot must be switched off before any work is done or the cover is removed.

Seems though that the replaceable modules are about £100 each (I have two of them) whereas the kit which includes those modules is about £35.
Hager pricing makes no sense to anyone.
Another example being that a single RCD is the same price as a consumer unit containing two of them and a main switch.
 
Hi all
Thanks for the replies. I was a bit wrong with dates - the SPD was fitted in Nov-2022, but still is less than 3 years old.

The supply type is TN-C-S therefore one of the modules would be redundant as it's shorted by the E-N link at the service head. So really if that 2nd module is red then it's got to be indicating end of service life, and likewise the same probably applies to the first module too. Perhaps the power blip that blew my monitors was a coincidence (they were on a different supply not protected by SPD).

I've asked Hager what the expected service life is for these devices as <3yrs seems a bit premature - and this lack of decent lifespan or the red indicator is likely something a homeowner won't even notice which leaves all their electronic gear vulnerable.

Thanks
Dave
 
therefore one of the modules would be redundant as it's shorted by the E-N link at the service head.
Not necessarily - what if any effects may occur depends on the length of the conductors between the service head and the SPD.
 
Afaict what the red window *actually* means is that the thermal protection in the surge protector has triggered and disconnected the surge protection element from the electricity system.

Surge protectors are designed to absorb short surges, but there is a limit to what they can absorb. If there is too much overvoltage energy then they will overheat and destroy themselves.

To me this seems like a fundamental design flaw, when faced with a surge too large for the surge protector to handle the surge protector will disconnect itself, but will leave the load connected.

Why both poles have triggered despite one being essentially shorted by the N-E link is a good question. One IMO likely possibility is that heat was able to pass from one side to the other, causing both sides to disconnect even though only one was producing heat. Another is that currents can flow in strange ways during high current surge events.
 
Hager SPDs display light red for fine and dark red for needing replacement, so really it depends what you mean by it displaying red in the indicator window.

I'm surprised no-one else has pointed this out to you.
 
I've read this since and mine show a frosted red appearance, so I presume they're ok?

From what else I read, the older units used to have a green/red indication but the newer ones just have red coming forward to the front of the window. Isn't it great to know the safety of all my electronic gear relies on how much red the indicator flags are!

I've asked Hager the expected lifespan of these and had no reply yet, as the red indication I believe is also to show end of service life. I'll ask the supplier as they'll probably have more clout with getting a response from Hager.
 
I've asked Hager the expected lifespan of these and had no reply yet,
There can be no answer to that as it depends entirely on how many and the magnitude of transient events that they are exposed to.
One could last for decades.
Another could be destroyed on the day it's installed.
 
Hi

Three quick(?) questions-

As it seems that a failure indication seems to depend on the amount of red shown, attached are two photos one of the SPD in the house and the other in the garage. Is there enough red in the garage photo to say that they have failed?

The garage is fed from the house, but the garage breaker stays on for about 10 seconds then trips – even with the main switch off. Is it possible that the SPD has failed ‘shorted’?

This started yesterday, up to that point I had not thought about an SPD in the unit, never mind noting the colour:)

Given that they are replaceable units (according to the documents), they look easy to replace?

Happy New Year!

H
 

Attachments

  • house_9738A.JPG
    house_9738A.JPG
    74.1 KB · Views: 25
  • garage_9739A.JPG
    garage_9739A.JPG
    69.5 KB · Views: 26
Hi

Three quick(?) questions-

As it seems that a failure indication seems to depend on the amount of red shown, attached are two photos one of the SPD in the house and the other in the garage. Is there enough red in the garage photo to say that they have failed?

The garage is fed from the house, but the garage breaker stays on for about 10 seconds then trips – even with the main switch off. Is it possible that the SPD has failed ‘shorted’?

This started yesterday, up to that point I had not thought about an SPD in the unit, never mind noting the colour:)

Given that they are replaceable units (according to the documents), they look easy to replace?

Happy New Year!

H
Hijacking another's topic, is very bad tactic.

is this is a new problem of your own? Your best way to get responses is to head to the red button tat the top of the forum, like this
Screenshot 2025-12-31 at 18.30.57.png

Then you'll get some attention.
Happy new year too.
 
...To me this seems like a fundamental design flaw, when faced with a surge too large for the surge protector to handle the surge protector will disconnect itself, but will leave the load connected...
OMG

Thisn is something I've been saying from the very start and everybody seemed to poopoo it
 
IME the prices on Hager's website have pretty much nothing to do with reality.
It is quite common. Not just in electrics/plumbing etc etc but in normal retail life too examples . Matchmakers 50p one flavour £1.65 a pack of three identical ) a long time ago that one) but recently Turkish Delight 38p one bar yet pack of three identical £1.45, catering ton of plum tomatoes a lot more per Kg than normal tins , loose sugar, bagged and weighed at point of sale a lot more than standard bags. Do they think folk don’t notice? Some of us do! It used to be rife in the TV industry in the 60s and 70s example 1k carbon resistors 100000 for £50 total and 500000 for £40 total - it was not unknown for the industry to massively over buy to get the prices down then throw the rest away until some of them had the idea to resell the excess to hobbyists suppliers at vastly reduced prices for them to sell on to hobbyists either in batches or as random mix. Quite often you find “normal prices” cheaper than “special offers “ if you look carefully and compare like with like.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top