I am completely new to this area so please be gentle and if you use any jargon, please include a brief explanation!
We have a combi boiler (Baxi Bahama 100). Domestic Hot Water works fine. Central Heating doesn't work at all. The CH circuit pipes running into and out of the boiler are both cold. The expansion vessel and internal piping gets warm, as the boiler ignites about every 6.5 minutes for about 6 seconds and then shuts itself off. This happens regardless of whether the boiler is in DHW-only or DHW+CH mode.
My first question: it seems that DHW is heated indirectly, through an exchange sink, from the CH circuit. A 3-way valve is used to switch the circuit being pumped through the heating element between a short loop (via the heatsink) and a long loop (via the radiators). Is this correct?
If so, given that the short loop seems like it's getting hot okay, it seems likely that the 3-way valve is stuck in the DHW position. This valve is a Honeywell VC6012, pictured below. As you can see, there is a white plastic switch on its right hand side. It can be pressed in a short distance, but springs out again when released (you can see the spring in the photo). It also looks as though it should slide along the groove, but it does not do so willingly (I have pressed as hard as I dare), whether I try it pushed in or sprung out.
Should I be able to slide the switch? If so, does this mean the actuator is all gunked up inside? Is it possible to open it up and fix it myself? If not, how difficult is it to fit a new one myself? (I have very little plumbing experience.)
Or am I barking up the wrong tree? I still don't quite understand why the boiler ignites at all when the system is in DHW-only mode and there is no DHW being drawn.
Thanks very much in advance for any insight,
Hamish
Update: I found the tech specs for the actuator at http://www.honeywell.se/energi/vceng.pdf.
There are 3 wires connecting it to the logic board: brown, blue and black. I probed them for AC and found that black is always live and brown is never live, regardless of whether I'm running hot water, whether the external timer box is calling for central heating, whatever. This means that the actuator is behaving correctly, always sending water to port A (the DHW loop). So do I need a new logic board?
I am completely new to this area so please be gentle and if you use any jargon, please include a brief explanation!
We have a combi boiler (Baxi Bahama 100). Domestic Hot Water works fine. Central Heating doesn't work at all. The CH circuit pipes running into and out of the boiler are both cold. The expansion vessel and internal piping gets warm, as the boiler ignites about every 6.5 minutes for about 6 seconds and then shuts itself off. This happens regardless of whether the boiler is in DHW-only or DHW+CH mode.
My first question: it seems that DHW is heated indirectly, through an exchange sink, from the CH circuit. A 3-way valve is used to switch the circuit being pumped through the heating element between a short loop (via the heatsink) and a long loop (via the radiators). Is this correct?
If so, given that the short loop seems like it's getting hot okay, it seems likely that the 3-way valve is stuck in the DHW position. This valve is a Honeywell VC6012, pictured below. As you can see, there is a white plastic switch on its right hand side. It can be pressed in a short distance, but springs out again when released (you can see the spring in the photo). It also looks as though it should slide along the groove, but it does not do so willingly (I have pressed as hard as I dare), whether I try it pushed in or sprung out.
Should I be able to slide the switch? If so, does this mean the actuator is all gunked up inside? Is it possible to open it up and fix it myself? If not, how difficult is it to fit a new one myself? (I have very little plumbing experience.)
Or am I barking up the wrong tree? I still don't quite understand why the boiler ignites at all when the system is in DHW-only mode and there is no DHW being drawn.
Thanks very much in advance for any insight,
Hamish
Update: I found the tech specs for the actuator at http://www.honeywell.se/energi/vceng.pdf.
There are 3 wires connecting it to the logic board: brown, blue and black. I probed them for AC and found that black is always live and brown is never live, regardless of whether I'm running hot water, whether the external timer box is calling for central heating, whatever. This means that the actuator is behaving correctly, always sending water to port A (the DHW loop). So do I need a new logic board?