Halstead Ace High Pressure issue

Joined
1 Dec 2007
Messages
1
Reaction score
0
Location
Surrey
Country
United Kingdom
Hi All,

I have a 3 year old Ace high which is serviced regularly but just recently it has started to vent large amounts of water from the external pipework.
the pressure has never gone above 2.5 but now it will start to drop as soon has the central heating is switched off. I have checked the expansion vessel and this is holding air and no water. It is also sitting around 1.5bar when i use a tyre gauge.
Can anyone advise me if this sounds like the PRV ? or any other suggestions.

Thanks in advance
H
 
Sponsored Links
You have to see if water is being discharged by the PRV.

If the pressure is 1.5 Bar cold then it should only increase to about 1.8 Bar hot. If yours is going higher then the EXV needs to be recharged properly.

See FAQ

Tony
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top