Hand Drier and Water Heater Rating on a single Spur

Discussion in 'Electrics UK' started by DIYWell, 5 Feb 2016.

  1. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    So, this is the situation ...

    Toilet, two cubicles, two hand basins and a hand drier. As far as I can make out, and I've not had time for a really good poke about, but there's a spur from the ring main to the 1.9kW hand drier via a switched, unfused connector then carries on to a 1kW water heater via an switched, fused connector.

    Now the water heater and drier have been there for at least 15 years and are showing their age; still work but the plastic is yellowing and I'm thinking of replacing them. If I move to an unvented undercounter water heater, it will look nicer and supply the two basins. Problem I've found is there seem to be very few low powered water heaters nowadays. Question to the expert on here, what power ratings can I go for before I seriously have to look at running more cabling?
     
  2. Sponsored Links
  3. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,892
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    Why don't we fit 1 sink and 2 hand dryers.

    I'm sure it takes people longer to dry their hands, than wash them :)
     
    • Like Like x 1
  4. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    It's not a great throughput loo. There's perhaps 10 folk in the office tops.
     
  5. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,198
    Thanks Received:
    556
    Location:
    London
    Country:
    United Kingdom
    Get the wiring sorted first. The hand dryer should not be on an infused spur. There should be a FCU at 13 a. This can also supply the water heater.
     
  6. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,469
    Thanks Received:
    4,203
    Location:
    Retired to:
    Country:
    Portugal
    Should you be doing work in commercial premises?

    To answer the actual question - 1.1 or 1.2kW.
     
  7. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    So you're saying both connectors should be fused to derate them?
     
  8. stillp

    stillp

    Joined:
    21 Sep 2009
    Messages:
    4,496
    Thanks Received:
    338
    Location:
    West Midlands
    Country:
    United Kingdom
    Do you have the necessary insurance to do this in a place of work?
     
  9. winston1

    winston1

    Joined:
    11 Jan 2010
    Messages:
    7,198
    Thanks Received:
    556
    Location:
    London
    Country:
    United Kingdom
    No. I'm saying there should be FCU before the hand dryer. The water heater can be on the same one.
     
  10. Sponsored Links
  11. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    Ah so supply to FCU to derate, then the output from it goes to drier and water heater
     
  12. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    Gads no I'm not going to do any of the work. Boss can bring in the trades to do all that. I've been tasked to get an idea of what's involved and see if there are any expensive surprises. Already spotted a different type of heater's needed so wondering if extra cable is needed, and since the building's a pig to work on, running new copper would be expensive, time consuming and disruptive
     
  13. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,700
    Thanks Received:
    280
    Country:
    United Kingdom
    The sensible option is to change the isolator on the hand dryer to a fused spur. Disconnect the water heater from the arrangement and run a new supply to it, size the supply to whatever size water heater you wish to have.... whether that be a 3kw unit with some water storage, or a 9kw instant unit.
     
    • Like Like x 1
  14. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    Yes. The sensible option. Yes. Problem is the sensible option in this building would involve lifting glued down carpets, floorboards, going through 2" thick joists and a 12" masonry wall just to get to the toilet, then there's more floor and tiles to lift. Sensible it may be but it rapidly becomes very expensive :(
     
  15. Adam_151

    Adam_151

    Joined:
    17 Jun 2004
    Messages:
    6,700
    Thanks Received:
    280
    Country:
    United Kingdom
    I suggest you get someone in to have a look, There is possibly an alternative route which has been overlooked.... and even if not, if one goes into a job like this on a Saturday morning when the office workers are all enjoying a lie in, then these things don't normally take too long.

    12" Masonry wall is pretty standard... my 'normal' set of drill bits for getting through walls that lives in the box with the drill are all 18" long.... I also have 1M bits, but I can count on one hand the amount of times I have needed them!
     
    • Thanks Thanks x 1
  16. Midas Man

    Midas Man

    Joined:
    4 Feb 2016
    Messages:
    50
    Thanks Received:
    2
    Country:
    United Kingdom
    Do you get paid any extra to 'sort' out the electrics?
     
  17. DIYWell

    DIYWell

    Joined:
    9 Nov 2009
    Messages:
    298
    Thanks Received:
    11
    Location:
    Edinburgh
    Country:
    United Kingdom
    We work for a charity. We don't get paid anything extra to 'sort' things out as you put it. If a room needs repainted, we roll up our sleeves and do it out of hours. If the floor needs cleaning, we do it ourselves. We have a very limited budget to bring in outside help because we try to disperse as much of our income as we can.
     