Hi guys, for the last few days CH system has been playing up. The heating comes on fine, but after a while the downstairs radiators cool down. I thought the actuator on the 3 port valve may be at fault but I have fully tested it today and it seems fine. Also removed the motor box and tried moving the valve by hand - it moves freely but only between the 5 to 12 and 5 past 12 positions which seems to be normal?
Found last night that turning the heating off and then on at the thermostat solved it for a while.
When it cooled again tonight (after about an hour of running) I went upstairs and checked out what was happening. The pump was running fine and the valve was still open for central heating. I turned the heating off and the valve closed and then there was a loud gurgling noise between the pump and valve. Switched it straight back on and the valve reopened and everything started to warm up again nicely.
Because all the electrics seem fine I am leaning toward the valve becoming blocked by sludge which clears when the valve is moved.
I would appreciate any advice before I take any further action on it.
Many thanks.
Phil
Found last night that turning the heating off and then on at the thermostat solved it for a while.
When it cooled again tonight (after about an hour of running) I went upstairs and checked out what was happening. The pump was running fine and the valve was still open for central heating. I turned the heating off and the valve closed and then there was a loud gurgling noise between the pump and valve. Switched it straight back on and the valve reopened and everything started to warm up again nicely.
Because all the electrics seem fine I am leaning toward the valve becoming blocked by sludge which clears when the valve is moved.
I would appreciate any advice before I take any further action on it.
Many thanks.
Phil