That selectric graph above is, IMO, wrong, can't see it circulating 0.6LPS, 36LPH @ 3.0M, that shoud read m3/hr, so 0.6m3/hr, 10.0LPM. I think the 95/100W super selectric actually circulates 10.0LPM @ nearly 4.0M, however we'll use the lower head of 3.0M.
If we assume that your system requires 3.0M to circulate 10.0LPM, then, because flow is proportional to the sqroot of Head, the UPS3 will circulate [email protected] (speed1), 13.17LPM@ 5.2M (speed2) & [email protected] (speed3) . Unfortunately, Grundfos's PP (propoptionl pressure) settings are far too low, running that pump on PP2(3.5M) will only result in a flowrate of [email protected], the Evosta3 (or the Wilo with its infinite CP&PPsettings) would give [email protected] since its PP2 head is 4.5M.
What mode/setting are you using just now?.
If we assume that your system requires 3.0M to circulate 10.0LPM, then, because flow is proportional to the sqroot of Head, the UPS3 will circulate [email protected] (speed1), 13.17LPM@ 5.2M (speed2) & [email protected] (speed3) . Unfortunately, Grundfos's PP (propoptionl pressure) settings are far too low, running that pump on PP2(3.5M) will only result in a flowrate of [email protected], the Evosta3 (or the Wilo with its infinite CP&PPsettings) would give [email protected] since its PP2 head is 4.5M.
What mode/setting are you using just now?.