Can someone help my velaire pj 90/110 old boiler has decided to keep it self warm even when the HW & CH controls are set to off both valves are closing and the pump not running boiler red light stays on. i have to switch off at the main supply when not in use
It is not a problem with the boiler.
They require only a switched live.
Are you sure the pump is not energised.
Do you have a frost stat that has been turned up.
It is not a problem with the boiler.
They require only a switched live.
Are you sure the pump is not energised.
Do you have a frost stat that has been turned up.
I have checked the zone valves are closing. Normally the red boiler light went out when the controls were set to off this now stays on and ocasinally the boiler fires up only warming the boiler. No frost or room stat only a potterton EP2000 control box Has worked great for many years is it possibly a contact that has stuck closed.
Hello again
MV's are both working fine open and shuting. Set up is fully pumped system no heat at the pump when control set off HW & CH when i switch the main system power on, boiler cold it fires up for a few minutes the shuts off the burner and cycles about every hour just keeping the boiler warmed up only pipe getting warm is the short length to the pump do you know if there is anything with contacts at the burner or boiler thermostats.
Regards
This makes NO SENSE - if the pump is shutting off correctly, and the system USED to work OK then someone has done something that they are not owning up to such as altering wiring and ending up with a permanent live to the boiler - there is no other logical explaination
This makes NO SENSE - if the pump is shutting off correctly, and the system USED to work OK then someone has done something that they are not owning up to such as altering wiring and ending up with a permanent live to the boiler - there is no other logical explaination
Hi Boilerman
I serverd my time as a marine engineer now 72 years old only me and the wife and she wont touch the boiler let alone the wiring. I agree with you it makes no sense what so ever. As we are extremly rural i did not want to call a heating guy due to the cost possibly min £90.00, if it was something i could fix.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local