Hi Hanni_han2008 welcome to the forum.
It would appear that you already have a room thermostat connected via the black and grey wires. That should be disconnected and removed. Then the two vacant terminals that presently have the grey and black wires in them.......
....would be connected to the Hive (Single Channel Version) terminals '1 Common' and, '3 Heating on'. It doesn't matter which way around that they go.
Finally the Hive needs a 230V supply connecting to N and L to provide it with operating power. This should come from the same 3A fused spur as the boiler. The N & L can be connected directly to the 'load' side of the fused spur, or the N and L boiler terminals, whichever is easier.
If the boiler has any built in time control, this should be set to be permanently 'on' 24/7, otherwise it will interfere with the operation of the Hive
If you have had to open up a room sealed compartment of the boiler to access the wiring terminals (This is not the case with all boilers, with some you do & some you don't) then it should have only been done by a RGI (Gas Safe Engineer) who can make the appropriate checks to make sure that it is sealed up again properly afterwards.
For next time, you should really have started your own new thread rather than tag your question onto someone else's. This is known as 'Hi-jacking' and is against the
Forum Rules. Also, when you start your own thread, it will be flagged as a 'new post' and seen more easily by those that can assist you, rather than being hidden away at the bottom of an old thread.