I have a 3 core 2.5mm SWA running from my house consumer unit to an external consumer unit in the garage. I've just upgraded this from a standard garage breaker to a RCD protected unit with 7 mcb's.
I've just been running through some figures in the TLC Volt Drop calculator to work out if I need to upgrade my current 2.5mm SWA.
These are my inputs
- SWA (3 Core) PVC
- Underground
- 2 of the circuits will be touching as they run through the same conduit (this is the 2.5mm supply cable to the consumer unit and the 2.5mm supply cable from the consumer unit to the shed)
- 3 KW of power
- Length of 10 metres
The calculator is saying my required cable size is 2.5mm and the MAX Cable Load is 16amp.
It doesn't look like I need to upgrade my supply cable from the house consumer unit, which is currently running off a 16amp breaker.
If I did however jump upto a 4mm supply cable, then running the figures through the calc and anticipate a higher usage of let's say 4kw then the current cable max load is 20amps. So therefore would a 4mm cable require a 32amp breaker?
Is there any harm in running a 2.5mm tail from the house consumer unit, to a 4mm SWA which terminates in the garage for a temporary period ?
I've just been running through some figures in the TLC Volt Drop calculator to work out if I need to upgrade my current 2.5mm SWA.
These are my inputs
- SWA (3 Core) PVC
- Underground
- 2 of the circuits will be touching as they run through the same conduit (this is the 2.5mm supply cable to the consumer unit and the 2.5mm supply cable from the consumer unit to the shed)
- 3 KW of power
- Length of 10 metres
The calculator is saying my required cable size is 2.5mm and the MAX Cable Load is 16amp.
It doesn't look like I need to upgrade my supply cable from the house consumer unit, which is currently running off a 16amp breaker.
If I did however jump upto a 4mm supply cable, then running the figures through the calc and anticipate a higher usage of let's say 4kw then the current cable max load is 20amps. So therefore would a 4mm cable require a 32amp breaker?
Is there any harm in running a 2.5mm tail from the house consumer unit, to a 4mm SWA which terminates in the garage for a temporary period ?