Hive receiver position

Joined
18 Jan 2006
Messages
431
Reaction score
7
Location
Cumbria
Country
United Kingdom
I want to fit a hive mini system in place of my current simple Homywell room thermostat. The installation instructions for these say to fit the receiver close to the boiler but can I fit the receiver in place of my current thermostat. It is a 3 wire type with live, neutral and switched live plus earth. It strikes me that this is all I need. Siting it adjacent to the boiler would not be a problem, it would just be easier to fit in place of the current stat. Do the fitting instructions presume you do not have a thermostat already fitted or that it is a 2 wire one?
 
Low voltage (230 volt AC) and extra low voltage cables should not be run together, so when using OpenTherm etc, you want the receiver near the item it is controlling, I am careful not to say boiler, as with older systems it may be controlling motorised valves, which in turn control the boiler.

Also with my own system, I have both Nest and Wiser so having the two receivers next to each other makes them easier to wire, but technically they could interfere with each other, the same applies with a receiver right next to the boiler.

So in real terms, if it works, and it is all using low voltage, you can put it where you want, as where ever you put it, it can cause problems.

What you want is all to be powered from the same circuit, so with a power cut unplugging the boiler from its normal supply and plugging it into an emergancy battery pack it will all work. You don't want any silly USB adaptors etc, powering a thermostat, so it will fail with a power cut. Neither of course unless battery back-up already built in, do you want a boiler powered by a FCU, plug and socket far better, makes it easy in a power cut. Also the lock off device for a plug is universal for a FCU you need the special one for that make.

But my house, the boiler is bottom corner of the building, and one of the TRV heads is top opposite corner, and the zigbee wireless connection can't reach, so I have to have a socket adaptor between the two to relay the signal, so to have the receiver centre of the house would be better, however the cables to allow it don't exist.
 
I want to fit a hive mini system in place of my current simple Homywell room thermostat. The installation instructions for these say to fit the receiver close to the boiler but can I fit the receiver in place of my current thermostat. It is a 3 wire type with live, neutral and switched live plus earth. It strikes me that this is all I need. Siting it adjacent to the boiler would not be a problem, it would just be easier to fit in place of the current stat. Do the fitting instructions presume you do not have a thermostat already fitted or that it is a 2 wire one?
Try it and see, I've done a few like that.
 
Not looking for anything complex. I am putting my house back on the market next year after a couple of chain breakdowns last year. When I previously had an ECP inspection, the house got a D rating. However, the inspector said the house was not too far from a C rating and not having any sort of smart heating control was one thing counting against it. Just trying to make the house more attractive without spending too much.
Boiler is a Worcester Bosch Greenstar combi by the way.
 