Same EICR as last post.
The CU has been marked as C2 due to a few holes that are larger than the regs. The holes are on the left side of the CU. The left side of the board isn't easy accessed and it would be very difficult to get fingers in anyway!
Can I put something (conduit?) in front of where they are to prevent access or do they need to be fully sealed? If so is intumescent silicon ok? I don't want to change the board.
Thanks