Hot water coming from expansion pipe into header tank.

Joined
10 Apr 2016
Messages
30
Reaction score
1
Country
United Kingdom
As Subject, have read other posts.
Running pump at slowest, faster gives more flow out of expansion pipe.
Boiler goes on and off so I assume its thermostat working.
Bleed radiators and pump.
Lowered level water in header tank when cold so when water comes from expansion pipe no water overflows.
Hot water from taps ok.
All radiators hot, so no blockages.

Is it bad to have this water coming out of expansion pipe?
 
Sponsored Links
Joined
14 Nov 2007
Messages
1,660
Reaction score
257
Location
Buckinghamshire
Country
United Kingdom
Yes, it will cause corrosion / sludge issue in the system. How is the feed and expansion connected to pipework?

Daniel.
 
Joined
10 Apr 2016
Messages
30
Reaction score
1
Country
United Kingdom
22mm copper pipe going up and past header tank and looping down so hot water falls into tank then from bottom of tank 15mm copper pipe to about 2" away from where the other left the system.

Is the corrosion/sludge caused then by the hot water passing through the air?
 
Joined
14 Nov 2007
Messages
1,660
Reaction score
257
Location
Buckinghamshire
Country
United Kingdom
22mm copper pipe going up and past header tank and looping down so hot water falls into tank then from bottom of tank 15mm copper pipe to about 2" away from where the other left the system.

No, the other side, eg, where do the expansion pipe connected to? Where do the feed pipe go to?
 
Sponsored Links
Joined
10 Apr 2016
Messages
30
Reaction score
1
Country
United Kingdom
Done a photo for you Stardanny.
from left Pump, Bypass, Hot water Coil, Input from header tank and Expansion pipe to header tank.
 

Attachments

  • SAM_0700.JPG
    SAM_0700.JPG
    132.8 KB · Views: 484
  • SAM_0701.JPG
    SAM_0701.JPG
    134.3 KB · Views: 484
Joined
14 Nov 2007
Messages
1,660
Reaction score
257
Location
Buckinghamshire
Country
United Kingdom
Air separater is the problem, probably be full of sludge with near blocked inside tube. Heated water goes to right side of air separater and because the left side is full of sludge or near blocked, heated water goes up via the vent pipe 22mm and come back via feed pipe 15mm back onto pipe after left pipe.

Air separater need to be replaced or clean out.

Daniel.
 
Joined
14 Nov 2007
Messages
1,660
Reaction score
257
Location
Buckinghamshire
Country
United Kingdom
image.jpeg

This is the air separater. If you have a magnet, put it on the tube and see if it stick. If yes, near blocked

Daniel.
 
Joined
10 Apr 2016
Messages
30
Reaction score
1
Country
United Kingdom
Nothing attracting a magnet.
Replacing might be a bodging type of exercise, its a solid brazed unit from pump connection to the 3 compression pipe connectors.
Cleaning I guess worth ago.
 
Joined
26 Jun 2004
Messages
64,368
Reaction score
4,699
Location
London
Country
United Kingdom
As far as I can see the separator can be removed with only a spanner.

Tony
 
Joined
10 Apr 2016
Messages
30
Reaction score
1
Country
United Kingdom
That air Sep had been cut out and unblocked before ;)
Sorry no, never been cleaned before, except for full system flushes.
Is it the compression connections that make you think that, if so not the case.
Up to those connections came with the built up cylinder c/w pump, this air separator, zone valves and appropriate pipe between.
 