Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Looking for a smarter way to manage your heating this winter? We’ve been testing the new Aqara Radiator Thermostat W600 to see how quiet, accurate and easy it is to use around the home. Click here read our review.
i do apologise, the pipe on top of the cylinder without the valve comes from the 3 way valve and gets hot, the other one with the valve goes through the floor.
ok, i will try and find air block. i understand the new valve does need replacing it was a needs must situation, however the ch is working fine, it is the hw that is not.
i would put some towels around the top of the cylinder.
shut that valve.
slacken the nut under the valve and let the water trickle out
that'll prove its not blocked and should clear any air.
you say you have two air vents.
if you have one on each pipe.
shut the 3 port valve to hw so its on heating only and open the bleed valve near the 3 port valve then it will pull water from the other direction
through the cylinder to the air vent and should release any air.
this sounds like a good idea however I do not know what position the lever should be in, I have just moved it from one side to the other and then the middle and did not know what for.
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local