Hello.

I hope you're all keeping safe and well.

I have bought a replacement built in oven in my new house without realising not all ovens are built equally.

This was my old oven (and current hob) https://www.beko.co.uk/built-in-fan-oven-and-ceramic-hob-package-qsf212x

The new oven is rated at 3.6kw. The manufacturer states that "it needs 16amps". The cooker came with a cable that ends in bare wiring. My cooker and hob sockets are connected to a control panel as pictured.

I understand that the only way to know if my wiring is good enough is to find the thickness of the cable. I can't see any writing on the grey cable.
DSC_0434_noexif.JPG DSC_0433_noexif.JPG DSC_0435_noexif.JPG
What do I need to do please?

Thanks.
 
The hob states it is 5.8kW which is 25A which is too much for a plug/socket and the 1.5mm² cable - although neither looks damaged by overheating.
 
I'm not sure about the circuit board fuse, I'll take a look.

I did think that 5.8 is way too much for the hob. Crazy.

Thanks for the link.

I will update
 
What is the rating of the fuse/circuit breaker that controls the cooker circuit?
OK, looking at the circuit board, i believe it is 32A.

Please see the photos. The labelling is done by myself. I'm not really sure what the leftmost fuse is for. I did have a previous immersion tank boiler which I got replaced with a combi boiler last year, but the leftmost fuse does not disable the new combi boiler.


Any comments?

Thanks.
 
Last edited:
Can you get a clearer image of the electrical rating plate of the hob?

Maybe a photograph of the inside of the hob plug would give us a better idea of the cable size.
 
1.5mm2 flex.

It appears to be 3 core.

As seen on the middle picture, you can use 5 core 1.5mm2 flex but not 3 core.

I can only assume you use just one or two rings at a time, if the 13 amp fuse in the plug hasn't blown.

Best follow EFLI's advice, and remove the socket, and connect the two appliances as he described - changing the hob flex for 3 core 2.5mm2 heat resistant flex.

Be sure to connect the hob correctly, as shown in the diagram using 2.5 3core flex.
 
All done and working. I used the flex that came with the oven.

Thank you so much for your help.

I can't thank you guys enough.

Yes, I only use two rings at a time, but only God knows how many rings the previous occupants used (or they replaced a blown plug just before putting the house on the market). I'm looking to replace the hob in the near future so I used the existing hob cable (yes, it is only 3 core, 1.5mm, but I will be replacing the flex with the correct one tomorrow when the store opens). Are electric hobs usually around 5.8 KW or is this one unusually high?

Finally, does the back box really need to be so big? Used the "related" back box: https://www.tlc-direct.co.uk/Products/AADCSB.html but there is SO MUCH empty space when done.
 
Last edited:
Are electric hobs usually around 5.8 KW or is this one unusually high?
That's pretty typical. With four of them, that's a little under 1.5 kW each (less than an electric kettle).

Don't forget that they are thermostatically controlled, and will hence be cycling on/off, very rarely 'in step' - so, even though they might add up to 5.8 kW if all 'on' simultaneously, in practice the average over any appreciable period of tuime would be a lot less than that, even if you were using all four.

Kind Regards, John
 
(y)

Finally, does the back box really need to be so big? Used the "related" back box: https://www.tlc-direct.co.uk/Products/AADCSB.html but there is SO MUCH empty space when done.[/QUOTE]
I am not sure about the surface boxes, to be honest, the one you link to does seem unnecessarily deep - perhaps someone else will know.

The cooker outlet will fit on a one gang flush back box because it doesn't matter that it overlaps a bit.
 