yes you can do it but certainly not straightforward and if you get it wrong new PCB time, do you have a small timer built into the Easi-heat ? you can only use the Hive mini single channel, you can not use the dual channel
Yes this in the correct manual as av not long had the boiler fitted. A was thinking if a ran a cables to x11 terminal from the hive receiver it would work ?
OK for future reference you have an Easi Heat i29C it is very important you quote the correct model when asking for advice they all wire differently the 29C is very different.
You need to supply a L&N to the hive mini receiver, this can come from either the L&N on the boiler or straight from the outlet on the same fused spur that feeds the boiler, terminals 1&3 go to the boiler terminals TA at terminal X11 at the boiler, you will have to remove the existing link
DO NOT make any links that you may see in other posts