Could somebody please explain the ignition sequence. (eg common, normally open, normally closed wires).
Also what would happen if the fan was to fail and the air pressure switch/micro switch? was stuck down.

Thanks
 
Sponsored Links
Sponsored Links
Im on a course,
Plenty of books,
Experience.. not much, but its helpful to hear answers from people in the know
 
General boiler workings and sequences are in plenty of books etc.

You'd be better off with a specific problem on a certain boiler for more info.

In order to your OP. The fan wont be sent power from the pcb if the APS is still in the N/O position. Most have 3 wires Common, NO and NC. It checks it is in the NC before powering fan.

rob
 
ignition sequence of a direct burner ignition for fan flued combi boiler

* demand for heat
*demand reaches PCB via interlocks
*Air pressure switch proves in normally closed position
*Fan runs
*Air pressure switch moves to normally open position
*Spark generator on
*Low fire gas solenoid opens
*Burner ignnites at low fire
*Flame proved by flame rec
*High fire gas solenoid opens
*Burner operates at high gas rate
*Flame constantly monitored by flame rec

i had to learn this for a british gas exam
 