Immersion heater problem

Discussion in 'Electrics UK' started by STI, 23 Mar 2014.

  1. STI

    STI

    Joined:
    5 Aug 2009
    Messages:
    426
    Thanks Received:
    27
    Location:
    Birmingham
    Country:
    United Kingdom
    Hi, I have an immersion heater that has a single element (physically) but is connected to economy 7. On the wall is a switch that states small or large, so I assume this means on small only some of the element heats up :?:
    Recently our hot water has not been getting hot, just warm. So that's my first point of confusion the "system" seems to be partially broken. Seems a bit like saying slightly pregnant.

    I have tested the stat and that does not appear to be working.
    I have tested the element and I am getting a reading of>99.99 I am using A MEGGER 1552 MFT, those who know this kit will know as well as giving a reading it has a open closed circuit indicator when set to Ohms. This indicator keeps switching open to closed and back again when showing the >99.99 reading.

    So I am guessing at the moment that my element has gone too. But what I cant understand is why am I getting warm water, if its not working it should be cold. Its been doing this for 3 days so I would have cleared any residual warm water in the tank.

    Can anyone advise
     
  2. Sponsored Links
  3. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,892
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    Do you have an RCD in the house?

    I little concerned your testing indicates a faulty stat and element which is unliky so questions your test method.
     
  4. STI

    STI

    Joined:
    5 Aug 2009
    Messages:
    426
    Thanks Received:
    27
    Location:
    Birmingham
    Country:
    United Kingdom
    Yes we do have an RCD switch protecting amongst others the immersion circuit.
    Testing method has been

    disconnect from supply

    For stat remove all connections. Place probes on both terminals with temp dial set to furthest point then move temp dial to opposite furthest point. No difference in reading

    For element remove all flex connections.
    Test across element terminals I get the readings previously stated

    The RCD has not blown, BUT when I tried to switch on the boost timer this did blow the main switch, not the RCD.

    This made me think if the element does have "two stages" when I use the timer boost does this use the full element, which then leads to the breaker blowing but explains why when I am on ECO 7 I am still getting a small amount of warm water and the breaker isn't blowing as it only uses the smaller section of the element.
     
  5. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,892
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    So maybe the stat is ok.

    What do you mean by the main switch tripping?

    If you have a dual element you should see 4 element ends and terminals.
    If normal single only 2.
     
    • Thanks Thanks x 1
  6. Sponsored Links
  7. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,556
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    First, set your MFT to measure resistance (not the low ohms setting).

    Measure across the immersion element. For a 3KW heater the element should be in the region of 17.5Ω

    Next measure across the stat. At lowest setting the reading should be open circuit. At highest temp setting you should see a short circuit (0Ω ).

    That should check if the components are OK. Come backl when you've done that.
     
    • Thanks Thanks x 1
  8. STI

    STI

    Joined:
    5 Aug 2009
    Messages:
    426
    Thanks Received:
    27
    Location:
    Birmingham
    Country:
    United Kingdom
    Yep done that.

    The stat reads 0.47 across the whole range of the dial setting

    The element reads >99.99

    By the main switch I mean the main breaker on the CU i.e. the switch that isolates all of the CU.
    Only two connections on the element (plus an earth)

    I have just connected the element to my PAT machine and I am getting an IR result of less than .10 so not a dead short but certainly well on its way.
    I guess this is why I am getting some warmth.
     
  9. Taylortwocities

    Taylortwocities

    Joined:
    28 Jul 2006
    Messages:
    20,556
    Thanks Received:
    2,132
    Location:
    Oxfordshire
    Country:
    United Kingdom
    That should tell you that the element fails the Ir test.
     
  10. Robin0577

    Robin0577

    Joined:
    16 Aug 2011
    Messages:
    577
    Thanks Received:
    109
    Location:
    London
    Country:
    United Kingdom
    Sounds like your element may have split open and part of your current path is now via the water rather than the element wire itself, not an uncommon occurrence with immersion heaters, especially in hard water areas.
     
    • Thanks Thanks x 1
  11. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
Loading...

Share This Page