What could be making an immersion heater trip when turned on at the switched fuse spur? It immediately trips on the main board. Thanks
 
Sponsored Links
What trips ,RCD, MCB, RCBO ?
Either a fault on the wiring,switch,or immersion element itself.
 
If you don't have any electrical test instruments, such as a multimeter, and knowledge of how to use it,then yes call an electrician
 
Sponsored Links
I can use a multi meter. I can test for resistance etc. What would I need.go test on the immersion?
 
Turn off Electric supply .
Remove the round cap from top of immersion.
Identify the live and neutral terminals of the immersion element and measure the resistance between them.
Should be around 19 ohms on a 3 kwatt element.
Also check between live terminal and earth terminal for a short circuit.
 