Correct. The circuit is maybe 10cm in trunking from the CU to the double socket.
Fair enough - but do you really mean 10cm?
We have had a freezer related trip/loss of an upsetting amount of food in previous house. It seemed like a good idea. Thoughts?
Most people probably would have some buried cable, which rather changes things. A dedicated RCBO is then probably what they would have to consider - although that would then leave the freezer at the mercy of 'nuisance trips' (which seem to be a problem for some people, even though not for me!). A 'non-nuisance' trip of the RCBo is not much of an issue, since it would usually mean that something had gone wrong with the freezer, anyway. The only obvious alternative would be to use something like SWA for the buried cable, or to have the cable in metal conduit (so as to preclude the requirement for RCD protection) but most would probably regard that as too much hassle!
In fact, whilst a house is occupied, it's probably best
not to have a freezer on a dedicated circuit - probably better to have it on a circuit whose loss will be more rapidly noticed (the same, in my opinion, with alarms). I have over-temperature alarms on all my freezers (which therefore detect failures of the freezer, per se, as well as lost power) - but, again, they are only of use when the house is occupied. However, at least in my case, even when we don't have a pandemic the proportion of time during which the house is unoccupied for a significant period of time is very small, so we would be very unlucky if a freezer were to fail, or lose power, during our absence - and I'm happy to leave insurance to deal with that very small risk if it ever happens!
Kind Regards, John