sh said:Having a TT system that is prone to nuisance tripping,would it improve the situation if I put in a second or even a third earth rod to reduce the earth resistance.
the only thing you can do is change the RCD. try changing it for a 100mA and use RCBO's for sockets/shower. changing the earth will not stop it trippingsh said:I currently have 30mA control on the incomer. This is what I am looking into at the moment. I think it is a combination of new kitchen appliances (oven, microwave combi, fridge/freezer and dishwasher) and older washing machine and tumble dryer.
Can you tell me the calculation for converting earth leakage mega ohms to RCD trip levels?
Thanks
You can't do that with a DVM - you need a proper insulation tester that zaps 500V down the cable..Careful_Bodger said:I was fairly rigorous with testing, as far as I could with a Fluke DVM, checking loop continuity and isolation. The latter encompassing L-N-E isolation within a circuit, and also circuit to circuit isolation on each wire.
You can't do that with a DVM
ban-all-sheds said:You can't do that with a DVM - you need a proper insulation tester that zaps 500V down the cable..Careful_Bodger said:I was fairly rigorous with testing, as far as I could with a Fluke DVM, checking loop continuity and isolation. The latter encompassing L-N-E isolation within a circuit, and also circuit to circuit isolation on each wire.
I know he said that. I can't think, though, what meaningful form of L-N-E isolation there is to test for other than insulation resistance...IanDB said:You can't do that with a DVM
No, he said ISOLATION, not INSULATION. Agreed however, that you need to check insulation as well, properly.