Indirect Coil Problem

Joined
19 Aug 2008
Messages
1,645
Reaction score
536
Location
Essex
Country
United Kingdom
As usual been round the houses looking for a solution before posting this topic.
Have a customer complaining that she has no hot water. She has an open-vented fully pumped system with an indirect hot water cylinder. With hot water ON the flow pipe into the cylinder coil heats up however the return pipe from the cylinder remains cold.

Could this be an airlock/blockage in coil etc?

btw - The pump is on its way out (I managed to get it working for a short while but it then died on me....customer advises that she has had problems with the pump for some time now).

Suggestions/solutions gents would be much appreciated.....
 
Sponsored Links
more than likely a airlock is there no manual vents or have u not cracked the cylinder connections
 
If its fully pumped system then you have answered own question ..pump.
 
Sponsored Links
you have checked that there is enough water in the system and no blockage? I had this in my old mum's system and was expecting a blocked F&E pipe junction, when I got my stuff together and clambered into the loft I discovered the F&E tank was empty due to a seized ballcock.

I am a householderr not a pro

on re-reading I agree - fix the pump

and as it is open vented I bet it has a good load of sediment
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top