The IET On-Site Guide BS 7671:2018+A2:2022 contains clear guidelines in the appendices for calculating the current requirements of circuits, taking into account diversity.
From Appendix A, Table A1, the current demand to be assumed for a Household cooking appliance is “The first 10A of the rated current plus 30 % of the remainder of the rated current plus 5A if a socket outlet is incorporated in the control unit”.
Doing the calculation for the Neff T69FUV4L0 Induction hob which is rated for 11.1kW @ 230V:
11.1kW @ 230V = 48.3A
10A + 30% of 38A = 21.5A
In other words, a 32A circuit is more than sufficient to power this appliance.
Further, from Appendix H4 “Cooker circuits in household and similar premises”:
“The rating of the circuit is determined by the assessment of the current demand of the cooking appliance(s), and the cooker control unit socket-outlet if any, in accordance with Table A1 of Appendix A. A 30 A or 32 A circuit is usually appropriate for household or similar cookers of rating up to 15kW."
Can you please ask your electrician to look at this again as I think the above information demonstrates conclusively that he/she is wrong to refuse on safety grounds to install or sign off the installation of this appliance on a circuit rated for 32A.