Is this 6mm or 10mm cable?

If you have a vernier gauge, measure the diameter of one strand, and count the number of stands of copper, in a core. From that, we can let you know the precise size.
So I finally got a vernier gauge which says a strand is 1.6mm. There are 7 strands.
 
diameter 1.6mm
radius 0.8mm

cross sectional area of strand πr²

3.14159 x 0.8 x 0.8 = 2.01 sq.mm.

2.01 x 7 = 14.074 sq.mm.


It means your measurement is not quite right - or the cable is between 10 sq.mm. and 16 sq.mm.
 
If yours really is 19*10mm² I think I'd be tending towards 16mm².

A quick google found this reply to a question

View attachment 408680
 
Thanks. It wasn’t an expensive vernier gauge but I calibrated it with something else and it was accurate.

I think the main thing is that it’s looking like it’s not 6mm cable - the strand diameter, the lug and the overall dimension all suggest something bigger.

Which at least means I can contemplate electric ovens /induction hob down the line.
 
diameter 1.6mm
radius 0.8mm

cross sectional area of strand πr²

3.14159 x 0.8 x 0.8 = 2.01 sq.mm.

2.01 x 7 = 14.074 sq.mm.


It means your measurement is not quite right - or the cable is between 10 sq.mm. and 16 sq.mm.
16mm² equates to 1.7059 1mm diameter - 10mm² equates to 1.3486mm

HOWEVER

1.6mm equates to 0.06299", could it be this imperial size,
1773687926105.png



ie pre 1970 or so and could be why no size markings - additionally imperial cables were bulkier than their metric conterparts.
 
Last edited:
It’s marked 1999 (which is when the extension was built). I just read imperial came in in 1970.

Would they have run a 6mm cable to feed a kitchen and bedroom/en suite (which used to have an electric shower)?

You can do that with 6mm aswell
For two double ovens and an induction hob?
 
Last edited:
It’s marked 1999 (which is when the extension was built). Is that likely to be imperial? Would they
have run a 6mm cable to feed a kitchen and bedroom/en suite (which used to have an electric shower)?

Then your measurement with your callipers must be wrong.
 

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Back
Top