I'm tidying up some wiring in the garage and fitting a consumer unit in the adjacent shed and have a query.
I have 2 x 2.5 cables exiting the house and entering the garage and they are both protected by the same fuse so obviously off the same circuit.
One cable supplys the garage socket and from this socket a spur has been taken to the small CU in the shed.
The other cable goes directly to the shed CU and I assume this completed the ring main.
Is this correct and would it be better to not spur off the garage socket to the CU?
Thanks.
Part P is known.
I have 2 x 2.5 cables exiting the house and entering the garage and they are both protected by the same fuse so obviously off the same circuit.
One cable supplys the garage socket and from this socket a spur has been taken to the small CU in the shed.
The other cable goes directly to the shed CU and I assume this completed the ring main.
Is this correct and would it be better to not spur off the garage socket to the CU?
Thanks.
Part P is known.