Isolator valves used on CH pipes

Discussion in 'Plumbing and Central Heating' started by jon92, 9 May 2020.

  1. jon92

    jon92

    Joined:
    23 May 2008
    Messages:
    140
    Thanks Received:
    2
    Location:
    Kent
    Country:
    United Kingdom
    Hello I'm hoping someone can tell me if these valves are OK on CH (vented) system? I've noticed the radiators downstream of them do not work unless pump is on full so I'm wondering if they are are for high pressure. Can't find them on the market now, could be up to 40 years old I think.
    Thanks for any help.
    20200509_112841.jpg
     
  2. Sponsored Links
  3. Terrywookfit

    Terrywookfit

    Joined:
    19 Jul 2007
    Messages:
    5,645
    Thanks Received:
    1,060
    Country:
    United Kingdom
    They are not full flow valves . The bore will be reduced and also probably restricted with rusty deposits.
     
    • Thanks Thanks x 1
    • Like Like x 1
  4. jon92

    jon92

    Joined:
    23 May 2008
    Messages:
    140
    Thanks Received:
    2
    Location:
    Kent
    Country:
    United Kingdom
    Thank you, that explains the chilly bedroom then! I will remove them.
     