Called out this morning. shower not working. went to the supply and fuse board first. Found a wylex rewirable with no spare ways, so the installer had wired off the supply side of the main switch into an rcd, then off to bathroom isolator. RCD has an I delta n of 0.03A and rated at 40A. An ironing board had depressed the test button. Guess the mistake?[/wiki]