Discussion in 'Electrics UK' started by AndyPRK, 28 Mar 2015.

  1. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,886
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    So what would happen in this scenario ?

    Wylex components.
    TT installation


    Main Supply into house >> 100mA TimeDelay RCD >> Switch fuses >> Consumer Units with single pole RCBO (e.g on socket circuit).

    You get a N-E short on the socket circuit.

    The RCBO trips, but can't isolate the N-E short.

    Will the TD RCD then trip turning off the whole house? And presumably the main RCD can't be reset until the fault removed or that CU main switch turned off.
     
  2. Sponsored Links
  3. Jackrae

    Jackrae

    Joined:
    20 Nov 2012
    Messages:
    2,240
    Thanks Received:
    377
    Location:
    Dumfriesshire
    Country:
    United Kingdom
    Unless the N-E fault exceeds 100mA for the duration of the time delay then I surmise it may (or should not) not trip
     
  4. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,632
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    We've discussed this one a good few times before. When there is an up-front TD RCD, one should not, at least in theory, use SP RCBOs - for the very reason you describe.

    Kind Regards, John
     
    • Thanks Thanks x 1
  5. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,632
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    That's clearly true but, in reality, true N-E faults will usually result in at least that much (persistent) current imbalance in the RCD - if not immediately then subsequently when someone turns on load(s) in the installation..

    Kind Regards, John
     
  6. Risteard

    Risteard

    Joined:
    18 Jun 2010
    Messages:
    2,182
    Thanks Received:
    158
    Location:
    Derry, Ireland
    Country:
    Ireland
    It is highly probable that it will.

    Use an RCBO which switches the neutral as well and then your S-type RCCB will discriminate correctly.
     
  7. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,886
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    Annoying, using RCBO's is actually worse in this case that dual RCD CU (in terms of keeping things up and running)

    Thankfully haven't got many RCBO's
     
  8. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,632
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    If all of your final circuits have RCD or RCBO protection then, AIUI, you will not usually** need to up-front Type S RCD, so you can rid yourself of that problem.

    [ **I say 'not usually', because my (TT) installation appears to be an exception to that rule. All my final circuits do have protection (RCDs in most cases, but three SP RCBOs as well). As far as final circuits are concerned, I do not need the up-front TD RCD. However, in fact I do (or, at least, believe that I do, and hence do have!) up-front TD RCD to provide the required fault protection for some long distribution circuits. I therefore theoretically should not have those three SP RCBOs - but I do, and in many years none of them has (IIRC) operated, for any reason, let alone an N-E fault, so I don't regard it as a major issue! ]

    Kind Regards, John
     
  9. Jackrae

    Jackrae

    Joined:
    20 Nov 2012
    Messages:
    2,240
    Thanks Received:
    377
    Location:
    Dumfriesshire
    Country:
    United Kingdom
    John

    Without wishing to highjack the thread you might be able to answer a question in a similar vein

    I have a TNS system with RCD on the main CU. From there a MCB feeder runs off to a lighting CU in which are installed a number of RCBO units feeding various lighting circuits (yes a big house). Occasionally, when a light bulb blows one of the respective RCBO units will trip. Question : what situations could cause the RCBO trip since there is obviously no connection between either L or N side of the failed filament. Could it be that the "twanging"" filament supports actually contact each other causing an instantaneous overload.
     
  10. Sponsored Links
  11. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,886
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    Humm I could get rid of the initial RCD's (actually old 500mA Chilton) at the moment but annoyingly quick to operate!

    Wanted to keep something there, as the cable isn't SWA to the remote CU's so should really have RCD protection (although its not really buried in walls)

    I think I've made my mind up.

    1) Use 100ma TD to a CU that has no RCBO's
    2) Ditch RCD to CU that contains RCBO's
     
  12. AndyPRK

    AndyPRK

    Joined:
    4 Jan 2009
    Messages:
    5,886
    Thanks Received:
    593
    Location:
    Herefordshire
    Country:
    United Kingdom
    Should have used a type C.

    Lamps blowing can cause type B MCB's and RCBO's to trip.
     
  13. EFLImpudence

    EFLImpudence

    Joined:
    7 Jul 2010
    Messages:
    37,460
    Thanks Received:
    4,199
    Location:
    Retired to:
    Country:
    Portugal
    RCBOs react to overload as well as faults to earth.

    …but there is a connection between L & N - the lamp.
     
  14. bernardgreen

    bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    25,822
    Thanks Received:
    2,571
    Location:
    Bedfordshire
    Country:
    United Kingdom
    When the filament fails a bit of it vapourises and a plasma discharge is created in the metal vapour. This is effectively a short circuit between Live and Neutral and can be several tens ( if not hundreds) of amps in some designs of lamps. Sometimes with small capsule type lamps the plasma shatters the lamp before the MCB operates.
     
    • Thanks Thanks x 1
  15. Jackrae

    Jackrae

    Joined:
    20 Nov 2012
    Messages:
    2,240
    Thanks Received:
    377
    Location:
    Dumfriesshire
    Country:
    United Kingdom
    Thanks Bernard, that makes sense (to me at least)
     
  16. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,632
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Perhaps the situation is a bit similar to my ('exception to the rule') one, then. As I see it, the concepts are no different for TT and TN, it's just that the devices differ. If the feed from meter to CU(s) is short and not particularly 'at risk', then that connection ('tails') needs no fault protection beyond that provided by the DNO's service fuse. If the distance is large (>3m generally gets quoted) and/or is 'at risk', then one has to provide upstream protection - usually a switch-fuse with TN, or the TD RCD with TT.
    That would certainly get (1) 'off the hook'. However, as I see it, as above, how acceptable (2) is depends on the length/routing of the path to CU (2). If it is long/'at risk' enough to need fault protection, then you shouldn't really 'ditch' the RCD.

    Kind Regards, John
     
  17. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    48,632
    Thanks Received:
    3,189
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Bernard beat me to it in explaining this to you. It's the overload part of an RCBO (i.e. the 'MCB' bit'), not the 'earth leakage' part, which can operate in response to the very high current which can flow for a very brief period (fraction of a second) whilst some types of lamps/bulbs are dying. The dame happens with MCBs.

    I have a TNS system with RCD on the main CU. From there a MCB feeder runs off to a lighting CU in which are installed a number of RCBO units feeding various lighting circuits (yes a big house). Occasionally, when a light bulb blows one of the respective RCBO units will trip. Question : what situations could cause the RCBO trip since there is obviously no connection between either L or N side of the failed filament. Could it be that the "twanging"" filament supports actually contact each other causing an instantaneous overload.[/quote]
     