Hi all
does anyone have an idea how to fix this, or what is wrong.
Power up, J1 (software version), Pause, click of relay, LED.s flash once & F3 code, pump running.
Will not reset.
This is a sudden occurance.
System was fine, went away for weekend, System was in Holiday mode. came back to an F3 code, and pump running.
I do not trust the handbook, Fault diagnosis of blocked heat exchanger.
As it has not been in use between being good, and showing the fault.
Checked PCB fuses. fine
No birds nests or blockages in the flue
Drained some water off no particles. Bar dropped, as expected. Re-pressurised, bar increased, so px sensor fine
Checked Diverter plunger operation by runnng hot tap. ok
Checked Diverter micro switch clicks, and goes oc cc as expected.
Bridged several sensors to isolate fault. took sensor resistance readings
High limit stat & thermistor not open cct - ok About 44 Ohm
Bridged CH thermistor gets F2 fault Thermister 333 ohm
Bridged DH sensor, no change 14.37K Ohm
Checked air sensor microswitch operation oc and cc and switch over when pipe sucked.
No power to Fan.
Fan free to turn, coil Resistance 43 Ohm.
There are no other sensors to check / spoof.
feels costly PCB, or Burner controller, or both
Any advice?????
does anyone have an idea how to fix this, or what is wrong.
Power up, J1 (software version), Pause, click of relay, LED.s flash once & F3 code, pump running.
Will not reset.
This is a sudden occurance.
System was fine, went away for weekend, System was in Holiday mode. came back to an F3 code, and pump running.
I do not trust the handbook, Fault diagnosis of blocked heat exchanger.
As it has not been in use between being good, and showing the fault.
Checked PCB fuses. fine
No birds nests or blockages in the flue
Drained some water off no particles. Bar dropped, as expected. Re-pressurised, bar increased, so px sensor fine
Checked Diverter plunger operation by runnng hot tap. ok
Checked Diverter micro switch clicks, and goes oc cc as expected.
Bridged several sensors to isolate fault. took sensor resistance readings
High limit stat & thermistor not open cct - ok About 44 Ohm
Bridged CH thermistor gets F2 fault Thermister 333 ohm
Bridged DH sensor, no change 14.37K Ohm
Checked air sensor microswitch operation oc and cc and switch over when pipe sucked.
No power to Fan.
Fan free to turn, coil Resistance 43 Ohm.
There are no other sensors to check / spoof.
feels costly PCB, or Burner controller, or both
Any advice?????