joist sizes for loft conversions

Discussion in 'Building' started by Railjohn, 17 Dec 2011.

  1. Railjohn

    Railjohn

    Joined:
    17 Dec 2011
    Messages:
    4
    Thanks Received:
    0
    Location:
    Cambridgeshire
    Country:
    United Kingdom
    I am coverting a loft into a railway room,and I want to remove parts of 2 collar ties.I have had drawings done by a structural engineer,these show that the existing 19mm chipboard flooring has to be replaced by 25mm chipboard.Thejoists are 3 by 2 inches,and there is supporting walls making the span for the joists between4 and 10 feet,although the new chipboard only covers 9 -10 feet either side of the centre.The collar ties are held in place by new 4 by 2 uprights bolted tothe collars and to the rafters.Are the joists man enough?
     
  2. mointainwalker

    mointainwalker

    Joined:
    24 Aug 2009
    Messages:
    2,461
    Thanks Received:
    240
    Country:
    France
    Well if the SE has done calcs for the floor thickness ( ?) then surely he must have considered the load on the joists .
     
  3. Sponsored Links
  4. ^woody^

    ^woody^

    Joined:
    3 Sep 2006
    Messages:
    33,999
    Thanks Received:
    4,615
    Location:
    West Mids
    Country:
    United Kingdom
    I can't believe that an engineer has spec'd 3x2 floor joists or that building control have approved them

    Even with the lightest loading and the closest spacing (400mm) they still wont span more than 1.1m - less than 4'
     
  5. RonnyRaygun

    RonnyRaygun

    Joined:
    4 Apr 2008
    Messages:
    1,843
    Thanks Received:
    260
    Location:
    Hertfordshire
    Country:
    United Kingdom
    Are the 3x2s existing?

    No, they're not man enough, anywhere near, to span 10 feet, half that if you're lucky.

    25mm chipboard is usually used where joist centres are 600mm.

    If your joists are going in at 600mm centres then you need 50x175 C16 to span 10 feet, which is what your SE should have specified, assuming standard domestic floor loads.
     
  6. DIYnot Local

    DIYnot Local

    Joined:
    3 Sep 2019
    Country:
    United Kingdom

    If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

    Select the supplier or trade you require, enter your location to begin your search.


    Are you a trade or supplier? You can create your listing free at DIYnot Local

     
  7. Sponsored Links
Loading...

Share This Page