Softus said:ollski - I'm not familiar with some of your terminology.
AR?ollski said:40 - 89% currently ncs will be AR in 2008
under 40% currently AR
If the boiler room is considered a compartment ie too small to be a living space anything less than 90% is AR
Does this apply if there is no vent into the room (i.e. the 'room being the living space)?Air from room:
hi 335 cm2
Lo 670cm2
And does this apply if there is?Air from outside:
Hi 168cm2
Lo 335 cm2
And does this apply if there is a 133mm diameter duct leading from the outside air?Direct room vent:
139cm2
softus the hi lo vents are only relevant if the boiler is in a compartment ie not large enough to be considered a living space ( although in London that could be a whole flat).
If the boiler is in a room standing on its own with a ducted vent with grills either end having no flyscreen, being non closable and with gaps between 5 - 10mm and of over 90% of the requirement (139cm2) it is fine.
If it turns out to be AR (at risk) this simply means the rgi turns it off at a user control and if the customer decides they arfe happy to use it they turn it back on and discharge any responsibility to the rgi.