Thanks. Please include everything connected to the 10 terminal block.Will draw out all the wiring on Monday.
Got that bit.As per average old system, the boiler had the old timer for CH & HW and it was remotely controlled by the Room stat in the hall at the other end of the bungalow. For our convenience I replaced this Satchwell R.Stat with the CM907 which worked for 18 months perfectly.
And that bit!With the recent problem ie
Recently this standard boiler timer went wrong & I fitted the potterton boiler digital Programmer BP2000.
That's the strange bit. I take it that the CH side of the BP2000 is set to continuous.Now this programmer seems to override the Honeywell room stat
Were you setting the operating times on the BP2000 when the CM907 was in place? or only when you replaced the old room stat?now I set the operating times required on the boiler new timer (BP2000), I replaced the CM907 with the old RoomStat just to see if it still works as before, which it does.
The same of cource is achieved with the CM907 set to "MANual" ie acts only as a roomstat (expensive one at £60) BUT we lost its "AUTO" function which looked after times & Temps.
Thanks for clearing that up.So you see I do not have installed & operating both simultaneously.
You should get continuity between A and B terminals when the thermostat is calling for heat. This should happen in both Auto and Man positions.As mentioned in last paragraph 5 posts earlier, if the 907 ought to test for continuity as the roomstat did, the fact that it did not it may be faulty.
What are the six time/ temperature settings on the CM607?