LED bathroom mirror
3 Jul 2012
West Midlands
Struggling to find concrete information on what wiring is needed for this...
Circuit is RCD protected, mirror would be in zone 2 (next to shower enclosure) so it will have to be IP44 rated. It will have a shaver socket.
Can I run some 3 core and earth from the lighting junction box to position on the wall?
I dont really want it coming on with the lights so I'll be looking for one with a switch.
Would i just leave the 3 core sticking out of the wall until I'm ready to fit the mirror? Most likely I will not wire at the junction box so its safe
IPX4 actually (the X meaning that part doesn't matter).
Next to shower enclosure may not count as zone 2.
The 600mm. measurement is taken from the edge of the enclosure like this -
It took me ages to find that diagram; they are nearly all wrong.
Are you counting the area around a basin as zone 2 as some people mistakenly report?
Basins do not create any zones; they don't count.
Socket must be to BS 61558-2-5 if in zone 2.
Yes - or 4 core flex
Ok. Switches are not allowed in zone 2 unless 12V with the power supply being outside of zone 2.
If you don't connect it, then, yes, it won't matter, will it?
@EFLImpudence
Its not 600mm from the side panel shower enclosure; its a 1200x800 tray so its at least 1200mm from the actual shower head on the adjacent wall but I doubt that makes a difference to the zoning rules. The recess between the side panel and doorway is approx 900mm so assuming a 500mm mirror you're looking 200mm from side panel
I was working on the seemingly wrong assumption that zone 2 is 600m above basin, but to be honest the shower is more important at this point
Ok, I might have to conceed on that one! By switch I mean the ones that are built in to the actual casing by the way. Not sure if that makes a difference
Ok. but that may not be the relevant figure.
No.
Yes, but how far is it from the the corner of the shower exit? See diagram.
Of course the shower is more important; the basin is irrelevant.
Yes, I realised what it was.
The regulations just say 240V switches are not allowed in zone 2 - but will it be in zone 2?
Will it not be like this where you have nothing to worry about?
Edited - drawn more to scale.
Just noticed that comment ...
... for clarity/completeness, I would add that a shaver socket would have to be to BS EN 61558-2-5 even if it were outside of Zone 2, unless it was more than 3 metres from the boundary of Zone 1 (i.e. edge of bath/shower).
Kind Regards, John