Firstly the short version: can XLG LED power supplies be used on a lighting circuit?
The long:
I am renovating a large room and this includes running relatively long lengths of RGB-CCT LED strip. I have a pair of Mean Well XLG-150-24 power supplies feeding 24V strips via a controller and amplifier (https://eu.mouser.com/ProductDetail/mean-well/xlg-150-24-a/) though may need them to uprate the power supplies in the end (final calculations of current draw).
I was (perhaps naively) assuming that being designed as LED power supplies I can connect them to the lighting circuit, which feeds the 3 reception rooms on the same 6A breaker. The total power and current @ AC voltage is well within what traditional incandescent lighting would consume so didn't expect it to be an issue. Since all I am doing is replacing the light fitting and don't need to modify any wiring, I figured I could do this work myself.
However the MCB is sometimes tripping when this circuit is first turned on. It's fine after flipping it back, whether output is loaded is or not. Now looking in detail at the datasheet I see there is a 50A inrush current specified. This makes me wonder if the cause is the caps charging when starting from cold; once charged it's fine. The spec says I should be able to use 4 PSUs (circuit breaker of type B) though, and even I need to upgrade to 240W supplies I should still be able to connect 2. Am I wrong in my assumption: should I simply not be using these supplies, and if so what should I be using? Should I have them wired to the socket circuit instead? Do I just need to replace the 6A breaker for a bigger one? (not sure if that last one counts as 'like for like' work I can do myself).
The long:
I am renovating a large room and this includes running relatively long lengths of RGB-CCT LED strip. I have a pair of Mean Well XLG-150-24 power supplies feeding 24V strips via a controller and amplifier (https://eu.mouser.com/ProductDetail/mean-well/xlg-150-24-a/) though may need them to uprate the power supplies in the end (final calculations of current draw).
I was (perhaps naively) assuming that being designed as LED power supplies I can connect them to the lighting circuit, which feeds the 3 reception rooms on the same 6A breaker. The total power and current @ AC voltage is well within what traditional incandescent lighting would consume so didn't expect it to be an issue. Since all I am doing is replacing the light fitting and don't need to modify any wiring, I figured I could do this work myself.
However the MCB is sometimes tripping when this circuit is first turned on. It's fine after flipping it back, whether output is loaded is or not. Now looking in detail at the datasheet I see there is a 50A inrush current specified. This makes me wonder if the cause is the caps charging when starting from cold; once charged it's fine. The spec says I should be able to use 4 PSUs (circuit breaker of type B) though, and even I need to upgrade to 240W supplies I should still be able to connect 2. Am I wrong in my assumption: should I simply not be using these supplies, and if so what should I be using? Should I have them wired to the socket circuit instead? Do I just need to replace the 6A breaker for a bigger one? (not sure if that last one counts as 'like for like' work I can do myself).