Hi
According to the installation handbook which came with my Grant oil fired boiler the bottom of the oil tank, supplying the boiler, needs to be 1.125m above the burner if a 10mm OD ( 8mm ID ) pipe is used in a single pipe gravity fed system. The pipe length is approximately 25m.
I want to keep the tank as low down as I can without affecting the operation of the boiler and still use gravity feed.
In order to lower the tank I could use 15mm OD pipe, however when I spoke to a local supplier they told me that they only ever supply 10mm OD pipe and set the bottom of the tank so that it is about 150mm above the burner.
Has any one got any comments ? Should I look to use a larger OD of pipe such as 15mm ?
According to the installation handbook which came with my Grant oil fired boiler the bottom of the oil tank, supplying the boiler, needs to be 1.125m above the burner if a 10mm OD ( 8mm ID ) pipe is used in a single pipe gravity fed system. The pipe length is approximately 25m.
I want to keep the tank as low down as I can without affecting the operation of the boiler and still use gravity feed.
In order to lower the tank I could use 15mm OD pipe, however when I spoke to a local supplier they told me that they only ever supply 10mm OD pipe and set the bottom of the tank so that it is about 150mm above the burner.
Has any one got any comments ? Should I look to use a larger OD of pipe such as 15mm ?