Whats more concerning is that you fail to understand the basic premise of supplementry bonding, True that the items are all earthed through their cpc's but the cpc's could be of different sizes therefore if a fault occured in say a towel rail and you were touching a radiator the fault current may flow through you and back to earth via the main equipotental bonding instead of the towel rails cpc because of the resistance of the cpc's.
The idea of the supplementry bonding is to bring all fittings to the same potential.