Hi,

I'm going to fit an extractor fan into a bathroom where there isn't currently one. The ceiling's 2.3m high and I plan to centre the hole at 1.8m. Doesthis sound okay and also, is there a minimum distance I need to put the fan from a window?
 
Sponsored Links
Joined
3 Sep 2006
Messages
35,948
Reaction score
4,984
Location
West Mids
Country
United Kingdom
Minimum 100mm in from the window jamb, and if possible 300mm from an internal corner of the room. And ideally in the opposite side/corner of the room to the door.

Use a core drill to save knocking the wall about

You may need a 10mm gap under the door to let air through
 