Looking for a replacement Central Heating Timer (Ed.)

It seems you may have a gravity installation, which the LP522 does support, maybe change it to gravity?
 
Sponsored Links
I made sure the switch on the LP522 was set to gravity before installing it on the back plate
 
  • Thanks
Reactions: CBW
It’s only the HW that’s gravity, the CH is pumped. The boiler fires up for the HW but not the CH
 
  • Thanks
Reactions: CBW
Sponsored Links
Ok, apology time the switch on the LP522 was on pump not gravity. I thought I’d slid the thing over to G but when I looked more closely, it’s not a slider it’s a tab that you have to move from sitting on one set of steel pins to sit on another set of steel pins…so in effect it doesn’t slide at all. Anyway, up and running now but thanks for your time and patience
 
  • Thanks
Reactions: CBW