Looking for some advice on what to do about old heating system

Thanks for that, I'll probably try it. I have an open system. It says to fill via the f&e tank. I take it I just pour it into the tank then drain some water from the system to allow the f&e tank to top up the heating system?
 
I'd empty the F&E tank via buckets etc. Then clean it. Drain a little further water out of the system, add the X400, then allow the F&E to refill. If you don't clean it before you start you'll wash any muck it contains into your system.
 
I'd go so far as to add, after sponging the tank clean, wipe it inside (including the lid, float and valve) with bleach. It's quite common for bacterial or fungal growth to occur after filling with clean water.

My guess is that the copper salts and other pollutants in the old water sometimes hold back growth.
 
Check your pump speed. One I looked at with similar symptoms had had people trying to improve the balancing and muttering about sludge, but the pump was on speed 1 out of 3. Speed 2 fixed it with one click. Speed 1 must always have been low, for the 3 bed house. You may well need speed 3.

Otherwise, you could do the old thing, which is to take out the offending rads to the garden and flush them with a hose - turn them upside down and back a few times when half full and keep at it until the water runs clear. You need a helper, but it's cheap to do :). (Pot/tube of jointing compound for the rad valves.)

While each rad's off you can turn the Htg on (CH only, but boiler stat OFF) with only that radiator's flow valve open, into a bucket. It's not a power flush but it's a lot more flow than it's used to and you'll be checking it's ok. If it's got 3/4" rad valve fittings, a garden hose connector or washing machine fill hose will fit, going to a drain.
If there's no flow, connect the outside tap to the drain end, (not open much, to begin with). Disconnect at the outside tap end every few seconds, and let it go to drain, to make sure you have water going up and down the pipe ok.
Be mindful of the level of water in the header tank, and check its overflow will warn you if it's getting full.

It'll take half a day but maybe save you £4k. That's nearly as much as I earn:cautious:.
 
Last edited:
Hi, thanks for that. Yeah about a year ago I took my living room heaters out (furthest from boiler and worst for heating up) and connected the mains water into them and flushed them through. It probably did help a bit.

My pump is set to 2. Again a service engineer told me that turning it up to 3 might be too much for the pipe work on my system. I've actually got no faith in the pump, I'm not sure if it needs bled but it doesn't seem great and could maybe be replaced
 
Too much? Hogwash! Did he suck in through his teeth at the same time? Combi boilers use the same pipe, 6 metre pumps, always flat out, usually pressurised to anything up to 30 metres head and pipework doesn't fail. A weepy rad valve if you're unlucky. Putting your pump up to 3 would raise the pressure by something around 1 metre!
Try it.
Your pump could be blocked or knackered, of course. Particularly if it's a Wilo, they don't like dirty systems.
 