I have an old vaillant bolier (combi about 12 years old) and we keep loosing pressure when the central heating is on, it seems fine when the Central heating is off.
We had a engineer to have a look at it a couple of times. He enjected the system with a leak sealer but after 4 days we still have the same issue.
It is really puzzling as we do not see any sign of water on the ceilings.
and there is no water coming from the safety valve on the outside wall.
When cold the pressure is 1.2 when hot 1.8. it is constant when hot but when it cools down it loses 0.4 each time.
any suggestions?