Lost in translation????

Discussion in 'Electrics UK' started by wv62, 5 May 2015.

  1. wv62

    wv62

    Joined:
    18 Apr 2015
    Messages:
    142
    Thanks Received:
    10
    Location:
    Mid Glamorgan
    Country:
    United Kingdom
    This is a warning sign on the outside of an inverter cubicle on a solar farm I worked at. It seems every cubicle by this company (a very well known multi national, not sure if I should name them as they employ me!) in the UK has the same sign. Do you think something was lost in translation??[​IMG]
     
  2. Sponsored Links
  3. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,248
    Thanks Received:
    3,254
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    :)

    Also, is it actually HV, in the IEC sense?

    Kind Regards, John
     
  4. wv62

    wv62

    Joined:
    18 Apr 2015
    Messages:
    142
    Thanks Received:
    10
    Location:
    Mid Glamorgan
    Country:
    United Kingdom
    The DC in is around 1000V and the outgoing varies depending on the DNO.
     
  5. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,248
    Thanks Received:
    3,254
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    1000V DC is obviously 'LV'. Is it likley that the output voltage would be greater than LV?

    Kind Regards, John
     
  6. westie101

    westie101

    Joined:
    3 Jan 2011
    Messages:
    2,497
    Thanks Received:
    313
    Location:
    Cumberland
    Country:
    United Kingdom
    Nice
    Particularly when the wording should possibly be

    "Danger of Death - Keep Off (or out)"

    Solar farms will usually output to the DNO at 6.6 or 11kv. though we have just had one connected at 33kV
    The control figure is the maximum load and the capacity of the local networks.
    We have generation sites connected at 132kV in places
     
  7. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,248
    Thanks Received:
    3,254
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Indeed - but maybe what they intended (but didn't get quite right!) was "Danger to Life" ?

    Kind Regards, John
     
  8. westie101

    westie101

    Joined:
    3 Jan 2011
    Messages:
    2,497
    Thanks Received:
    313
    Location:
    Cumberland
    Country:
    United Kingdom
    Oh I got that straight away
     
  9. ericmark

    ericmark

    Joined:
    27 Jan 2008
    Messages:
    18,963
    Thanks Received:
    1,782
    Location:
    Llanfair Caereinion, Nr Welshpool
    Country:
    United Kingdom
    Maybe written by Mary Shelley author of Frankenstein!
     
    • Thanks Thanks x 1
  10. Sponsored Links
  11. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,642
    Thanks Received:
    387
    Country:
    United Kingdom
    That depends on the earthing arrangements. A +-500V (relative to earth) system would be LV but a system with one end grounded and the other at 1000V relative to earth would be HV (by the BS7671 definition). I'm not sure about floating systems as "nominal voltage relative to earth" would be undefined in that case. I'm not sure if that means you should ignore the earth relative part of the definition or if you should assume the worst.
     
  12. wv62

    wv62

    Joined:
    18 Apr 2015
    Messages:
    142
    Thanks Received:
    10
    Location:
    Mid Glamorgan
    Country:
    United Kingdom
    Hmmm.....Just got an image of being chased around the field by an inverter :eek:
     
  13. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,248
    Thanks Received:
    3,254
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Eh? The BS7671/IEC definition of LV goes up to 1500V DC, doesn't it?
    Indeed. The BS7671 definitions really 'fail' when the supply is floating relative to earth!

    Kind Regards, John
     
  14. plugwash

    plugwash

    Joined:
    28 Mar 2004
    Messages:
    9,642
    Thanks Received:
    387
    Country:
    United Kingdom
    AIUI it's 1500V between conductors but only 900V relative to earth.
     
  15. JohnW2

    JohnW2

    Joined:
    28 Jan 2011
    Messages:
    49,248
    Thanks Received:
    3,254
    Location:
    Buckinghamshire
    Country:
    United Kingdom
    Ah, yes - I forgot about the 900V :oops:

    Kind Regards, John
     
  16. ban-all-sheds

    ban-all-sheds

    Joined:
    27 Aug 2003
    Messages:
    69,782
    Thanks Received:
    2,858
    Location:
    London
    Country:
    United Kingdom
    Here's a suggested warning notice:

    [​IMG]

    It avoids all the problems with ELV/LV/HV terminology and has the added bonus of meaning electricians only need to carry one type.
     