House is 1992 build Timber Framed. Main House CU is an old Wylex that had Fused Wire type Fuses, but have been changed out for Wylex MCBs at some point. The Garage is fed from this through a 20A MCB to tghe Garage CU ( old )Fused type also. ) My intention is to have both replaced with New RCBO type CU's. The Garage has one Lighting Circuit 6A MCB and two 16A MCB Radials. One Radial feeds two Double Sockets, That don't have any heavy consumers except for a Tumbler Dryer). The Other Radial supplies Oil Boiler and one Double socket that just has a Freezer Plugged in .My Question is
I want all circuits to be on RCBO's. Because the Freezer is in the Garage is it Possible for the feed to the Garage from Main CU to remain on a normal MCB as the Garage circuits would all be on their own RCBOs anyway. My thought is that this would give the Freezer some redundancy, because anything in the Garage that would make an RCBO trip on the Main CU in the house would also cause the Freezer to loose Supply .
Hope I've got this across. Any thoughts on this pls . It would be nice to have some Idea before I start looking for Electrician to do the work.
Thanks
I want all circuits to be on RCBO's. Because the Freezer is in the Garage is it Possible for the feed to the Garage from Main CU to remain on a normal MCB as the Garage circuits would all be on their own RCBOs anyway. My thought is that this would give the Freezer some redundancy, because anything in the Garage that would make an RCBO trip on the Main CU in the house would also cause the Freezer to loose Supply .
Hope I've got this across. Any thoughts on this pls . It would be nice to have some Idea before I start looking for Electrician to do the work.
Thanks