Can disconnectted ring circuits pick up mains at a high enough level so that you can measure say 10V ac between the disconnected live and N. Also can momentarly connecting the disconected live to N or earth cause an RCDs to trip? Thanks
if using a high impedance meter then yes indeed you can get much higher readings than that. However they should drop away at the slightest hint of a load.
curious67 said:
Also can momentarly connecting the disconected live to N or earth cause an RCDs to trip? Thanks
no but connecting the still connected neutral and earth to each other through a low resistance object (e.g. a knife blade) is almost gauranteed to take out a RCD!
If you`re getting a voltage it could be from inductance or capacitance. But you`re RCD question makes me think also about insulation resistance.
Are you sure you`re N is properly disconnected completely?
As our friend said - the smallest load should dimish it significantly.
With appliances plugged in, shorting L to E will trip the rcd with the live dead(or alive).
Shorting N to L will not cause the rcd to operate. It may if you have the circuit off, and the insulation resistance isn't good (in circuit or appliance).
I'm was using a high impedance multi meter (hence the volts) and of course a momentary N to E short will modify other connected ring ctt flow & hence trip the RCD. I was adding a spur to a ring. I just wanted to have an explanation for the symptoms. Thanks
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local