Au contraire! See this set of beauties readily available on a well-known auction site!You cant get 15a fuses that go in plugs.
I would agree with a domestic appliance one would expect that to be the case, however with commercial equipment often the protective device needs to be where there is access to service it, this is not always possible inside the appliance, and I am sure you have fitted many a motor starter which is a different make to the motor, I know I have.As has been said so many times, if a manufacturer believes that their product requires protection which may be greater than that provided by the device protecting the cables which supply it, then they should provide that protection within the product.
But not to BS 1362 the last 2 do not comply, yes you could get 15 amp plugs where the pin was a fuse, but not seen them for some time now.Au contraire! See this set of beauties readily available on a well-known auction site!
If the manufacturer installs a protective device in an 'inaccessible' location,then they are, at the least, plain daft - it could easily be rendered 'accessible for servicing' (often on the front panel' of the equipment).I would agree with a domestic appliance one would expect that to be the case, however with commercial equipment often the protective device needs to be where there is access to service it, this is not always possible inside the appliance, and I am sure you have fitted many a motor starter which is a different make to the motor, I know I have.
Do you have a link for them ? Tempting.Au contraire! See this set of beauties readily available on a well-known auction site!
A simple google search was all that was needed.Do you have a link for them ? Tempting.
I have someAnd we would all assume they were fakes? ... Or not to British standard. ... Better than a nail I guess
True.The good thing about them is that they should would generate Less heat.
Possibly, but certainly not necessarily, at least in relation to fairly modest 'overloads.. We obviously don't have any data on the "20A" fuses, but if one extrapolates from 13A BS1362 fuse, it could take something like 34A to blow a 20A one - which, in theory, should not cause a B32 to operate (which should take at least 36 to trip. In the case of a very high fault current then, yes, it would be pretty likely that the MCB to probably operate first (with any fuse rating).And let the MCB trip before the fuse which is typical.
Maybe, but it wouldn't surprise me if the socket was also happy, at least with 15A. Don't forget that the BS1363 'temperature rise test' is done with 14A through one of the socket outlets.The plug would be up to it. It’s more the socket I worry about
Until suddenly it isn't.As a DIY user latching on the on/off button may be considered as a good thing.
I would be far from surprised if they actually 'do what it says on their tin', in the same way that do the (BS1362-compliant) ones from 1A to 13A.
That's not much different from the "at least 36A" I mentionedThe fusing current of a BS1362 fuse is 1.9*In, i.e. 38 A for the 20 A one.
Well, the magnetic threshold is. However, relevant to 'moderate' overloads (i.e. not 'shorts') a B-curve MCB should operate (thermally), eventually, for any current above 1.13 x In - i.e. about 36.2A for a B32.The fusing current of a B-curve MCB is 1.45*In or 46.4 A for a B32.
Yes, that's essentially what IO wrote. However,there is some 'hit and miss'about it, and I've seen examples of both the things that "one would not expect" - a 13A fuse, but not a B32 operating in the face of a high current fault ('short') or an MCB, but not a 13A fuse, operating in the face of a 'moderate overload' - so one can never be certain (and, of course, sometimes both will operate).So in case of an overload it’s likely that the fuse blows first - provided this plug is the only load on the circuit. In case of a short, the MCB is most likely to trip first with at least a 13 A fuse.
I largely agree with all that - but, as I've said, I'd been far from surprised if a 13A plug + socket could (at least usually) cope with 15/16A, and maybe also 20A (or more).Looking at a BS1363 plug I suspect the weak spot is the fuse holder. All other parts seem quite likely to withstand much higher currents, possibly up to 32 A (nominal current, not under overload conditions) if you managed to cram 4 mm2 conductors into the terminals.
The sockets are a bit of an unknown. I don’t doubt they could be made to warrant a 32 A rating but I‘m not sure they actually are. The contact surface between plug and socket is probably equal to that of a 32 A industrial socket, which is a good start. The questionable bits are the connections between the screw terminals and the contacts, and of course the switches.