- Joined
- 27 Jan 2008
- Messages
- 29,355
- Reaction score
- 3,608
- Location
- Llanfair Caereinion, Nr Welshpool
- Country
Some heating appliances have a voltage and wattage range, my cooker has this, and as such one can work out what the watts are at a set voltage, however unless the range is published, one can't assume, we also can't rely on the voltage being less than 230 +10% or 253. Yes often it is at 230 volt, but with micro generation the voltage can today cover the whole range 216.2 to 253.No, it isn't.
Showers are primarily quoted at 240V, e.g. 9.5kW @ 240V = 39.6A.
This is not a coincidence. It is so they may be on a 40A MCB.
The quote may also mention that 9.5kW @ 240V = 8.7kW @ 230V. This latter figure is only 37.8A.
Therefore you may have a slightly higher wattage if you are designing at 230V, although this may not be wise, as (as Winston is always telling us) the actual voltage is likely to be around 240V.
So all we can do is work it out at 230 volt and expect manufacturers to allow for the permitted under or over voltage.