Kitchen sockets on a 40A without RCD protection - really ?


Missed that, I suppose, with 6 mm² radial one could, but installation methods 101 to 104 will not allow 40 amps with 6 mm² and one would not get larger cables into the sockets, so yes something seems wrong there. Also, sockets on non RCD protected circuit.Kitchen sockets on a 40A without RCD protection - really ?
True, but the majority of domestic wiring is Method C, in which case 6mm² cable would support 40 A.Missed that, I suppose, with 6 mm² radial one could, but installation methods 101 to 104 will not allow 40 amps with 6 mm²
True, but the majority of domestic wiring is Method C, in which case 6mm² cable would support 40 A.
However, I would have thought that a 6mm² radial sockets circuit would be very unlikely - unless, I suppose, it had been intended as, and/or 'repurposed from', a 'cooker circuit'.
I don't think that would make any difference (and would offer no real benefit over a 6mm² radial), since the 'ring part' of the lollipop would presumably also have to be 6mm², since even Method C 4mm² doesn't have quite enough CCC to be adequately protected by a 40 A OPD - and a bit of that cable would carry almost 40A if the total design current were applied close to 'the origin of the ring-part of the lollipop' (and there's obviously no corresponding 'dispensation' in relation to overcurrent protection such as exists in BS 7671 for 30/32 A ring finals)maybe a lollipop circuit - still don't think a 40A MCB is appropriate
I don't think that would make any difference (and would offer no real benefit over a 6mm² radial), since the 'ring part' of the lollipop would presumably also have to be 6mm², since even Method C 4mm² doesn't have quite enough CCC to be adequately protected by a 40 A OPD - and a bit of that cable would carry almost 40A if the total design current were applied close to 'the origin of the ring-part of the lollipop' (and there's obviously no corresponding 'dispensation' in relation to overcurrent protection such as exists in BS 7671 for 30/32 A ring finals)
Speculating about what? I merely stated the facts about the CCCs of cables and the maximum rating of OPD which would adequately protect them (at least, in the eyes of BS 7671).You’re speculating ...
It would certainly be a bit of a struggle with many, maybe most.... and lots of cheap accessories won’t accept 2 x 6mm cables
Speculating about what? I merely stated the facts about the CCCs of cables and the maximum rating of OPD which would adequately protect them (at least, in the eyes of BS 7671).
It would certainly be a bit of a struggle with many, maybe most.
However, why are you telling me this (which we all already knew)? The idea of having any sockets circuit wired with 6mm² cable seems totally far-fetched to me - it was eric who brought 6mm² cable into the equation, but merely to indicate that it was the smallest cable that could be ('compliantly') protected by a 40 A OPD (which is correct), but I don't imagine that even he believed that 6mm² cable was what the OP has!
I don't think anyone has said it's "OK" - as you say, we don't know enough.Well let’s allow the OP to have a proper inspection so they can tell us how it’s actually configured but how ever you look at it it’s currently impossible to say it’s ok - simply not enough data or facts to go on
Maybe, but all of this has got absolutely nothing to do with the OP's question about his light, which may well not have been plugged into a socket in the kitchen, anywayWe might even find what’s labelled kitchen sockets may actually be a shower or out building


Since there is a 13 amp fuse in the plug, it can not be overloaded, the bulb should also contain a fuse, so that the 2 amp rating of a B22d lamp holder rated at 2 amp is not overloaded.If, as you frequently say, the U.K. light circuit is 6A because the switches etc. are only rated for 6A, how do you feel about 13A sockets being on 32A circuits?
well, not overloaded beyond 22 A or so.Since there is a 13 amp fuse in the plug, it can not be overloaded ...
incandescent bulbs did, implicitly, have a 'fuse', otherwise known as its filament - which would almost certainly blow at currents a lot less than 2A. I think that most/all LED lamps/bulbs have a 'fusible link', which very commonly has melted when the lamp dies., the bulb should also contain a fuse, so that the 2 amp rating of a B22d lamp holder rated at 2 amp is not overloaded.

They should have an independent fuse, the idea was if when the filament ruptures you get ionisation, the bulb's fuse will rupture before the main fuse ruptures, however when we changed from fuse to MCB, the MCB was too fast, and would often trip before bulb fuse ruptured.incandescent bulbs did, implicitly, have a 'fuse', otherwise known as its filament - which would almost certainly blow at currents a lot less than 2A. I think that most/all LED lamps/bulbs have a 'fusible link', which very commonly has melted when the lamp dies.
this one type 4, but many no marking as to type. And on the caravan site I was stopping at, someone worked out by screwing in the yellow screw,
they would trip at a higher current, we had 6 amp supplies as the whole supply to the site was 100 amp split phase, and this resulted in the standard kettle not working, I remember talking to the site owner, and he would go around with a 2 kW heater and see if they would trip, if not change them.If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.