... Assuming of couse that he is measuring phase-> neutral... IIRC the metrel is capable of doing a 415v loop reading (but I never use that, just double the highest SP value... its the way I was taught... saves you blowing up someone elses test equipment!)
A value that low is going have quite a bit of error/uncertaintly... perhaps if rob presses the test probes on better he might see a higher fault level
, chances are he will if he pulls some overtime and tests when network loading is low
,if you are thinking about what the tester is doing... its applying a load of 23A, recording the volt drop and applying ohms law to give an impedance, you start to see that it becomes very difficult to measure low impedance fault paths accuratly (same again with high values of insulation resistance... but luckily, the differece between 800meg and 1000meg is largely irrelevant!)
Not that a fault of that magnatude will over occur IRL, in real life faults don't involve a silver dagger 10mm along the submain from where it leaves the panelboard
,plus the inductance of the supply transformer means that currents of that manatude don't just instantly start flowing... there it'll take a a small fraction of a second to happen, and the fuse will have opened by then
(and even before it does, the reistance will have increased)