I just want to clarify the 'Loop' settings on the MFT1552 I have.
Single phase - If I was checking Zs on a RCD or non-RCD protected circuit I would put it on 'NO TRIP', or if I was checking Ze I could put it on 'NO TRIP'. (using red, black & green wires for testing)
Single phase & 3 phase - If I was checking Zs on a non-RCD protected circuit only I would put it on 'HI', or if I was checking Ze I could put it on 'HI' aswell. (using red & green wires for testing)
For checking PFC I could put it either on 'NO TRIP PFC' or 'HI PFC' & for checking PSCC I put it on 'HI PFC'
Can any other MFT1552 users tell me what they use.
Thanks.
Single phase - If I was checking Zs on a RCD or non-RCD protected circuit I would put it on 'NO TRIP', or if I was checking Ze I could put it on 'NO TRIP'. (using red, black & green wires for testing)
Single phase & 3 phase - If I was checking Zs on a non-RCD protected circuit only I would put it on 'HI', or if I was checking Ze I could put it on 'HI' aswell. (using red & green wires for testing)
For checking PFC I could put it either on 'NO TRIP PFC' or 'HI PFC' & for checking PSCC I put it on 'HI PFC'
Can any other MFT1552 users tell me what they use.
Thanks.