Hello

I am installing a consumer unit, circuits and storage heaters on friday for an off peak supply. A dual tariff metre and tails will be there.

The size, length and material of the tails will be the same as the existing cu give or take a few cm's. So in order not to have to do the Ze and pfc at an unsociable hour, would it be reasonable and correct to take the Ze and pfc reading from the existing cu and use that as a Ze for the new cu figure. I can obviously add my R1 + R2 to get ZS. Luckily the new circuits will be run in such a method that RCD protection is not required.

Regards
 
Sponsored Links
Joined
31 Mar 2006
Messages
20,009
Reaction score
1,383
Location
Leeds
Country
United Kingdom
Yes that's fine. Take a Ze reading from the peak supply and then verify continuity from the MET to the OP CU.
 
Joined
30 Jun 2009
Messages
21,627
Reaction score
2,568
Location
Londonderry
Country
United Kingdom
Why would it be a problem taking the Ze when new CU is installed?
and why are you calculating Zs and not measuring it?
 
Joined
7 Jul 2010
Messages
39,235
Reaction score
4,873
Location
Retired to:
Country
Portugal
I think it would be reasonable to assume (never assume) that the Ze should be the same.

However, you should do the test to determine that it actually is the same.
I.e. the conductors, especially earthing conductor, are connected satisfactorily.
 
Sponsored Links
Joined
29 Jun 2008
Messages
834
Reaction score
46
Location
West Midlands
Country
United Kingdom
Regards Gentlemen.

To PBoD, I understand your questions but I do not want to be waiting around or returning a midnight waiting for the off peak to energise.
 
Joined
11 Jan 2004
Messages
39,724
Reaction score
2,017
Country
United Kingdom
I can't see a problem with using the Peak tails to provide power and connecting your croc clip to the OP earthing conductor.
 
Joined
18 Jul 2004
Messages
8,518
Reaction score
406
Location
Devon
Country
United Kingdom
With two CU's next to each other, I would pickup the live from the peak supply and the earth from your new board. If the tails are visible and short, there is no issue here at all.

On new installs, the prefered method is to measure the R1+R2 of the final circuits, calculating the Zs. You do not have to test both the R1+R2 and the Zs, but both columns need filling in on the paperwork. As you MUST carry out the R1+R2 (as it is a required dead test before energising), there is no point in then carrying out a Zs too.

When doing a periodic, you can do a Zs if you find it easier than an R1+R2 as the circuit is already energised.
 